Heat is transferred from refrigerant to outside air between the compressor and expansion valve = hot air. The latent energy in hot air has the ability to carry more moisture than cold air. Most people situate their HVAC units on the exterior for good reason. Seldom in the attic. This attic is being used as an exterior shed for the unit. |
Nowhere did the OP say the compressor was in the attic, just the air handler. The problem with attics isn't that they get hot. It's that at night in the winter they get cold. Any moisture that leaked through the ceiling condenses. |
Correct. |
AHU and ducting insulated? |
There's no good way to install an AHU in unconditioned space. |
|
Thank you so much for this very helpful discussion! We really get that it is all about moisture thanks to your comments. OP here to clairfy:
1. Our goal is to finish the attic into living space. 2. It is correct - we have just the air handler unit in the attic and the compressor is outside. This is how it was when we bought our home. 3. Our current thinking is to wall the air handler unit into the conditioned space we are making. And use a smart membrane product like intello or membrain to prevent moisuture from reaching cold surfaces in the walls and rafters. Combined with an unfaced batt insulation. What do you all think? |
Works. The fan and evaporation coil don't need anything special around them if the entire attic around them is insulated. That would be the same as having it in a closet in most homes. Would be good to make a little closet space around it to reduce the noise coming from it, though it will still be loud due to the air intake vents in a more confined space like the attic. Just make sure to check and perhaps update the condensation drain lines. |
|
Look up spray foam, attic and uninsurable. You could also look up unmortgageable but that’s a mouthfull.
Rockwool and you don’t need foam jockeys |
Op here, what would you suggest doing in this situation? |
Rockwool and you absolutely, absolutely need vent channels between the insulation and the sheathing. If the roof isn't already vented at peak and eave this may not be feasible. If the roof can't be made to be vented spray foam is really the only solution. The other alternative would be foam on the outside between the sheathing and the shingles, but that would require re-roofing. |
A smart membrane is good, but it is in no way sufficient to protect the roof from condensation. You need either ventilation between the insulation and sheathing, spray foam, or insulation on the exterior. |
| Thanks! This is very helpful. |
Agree with everything but the conclusion (Rockwool beats fiberglass in every way) and would add don’t fall for borate treated cellulose either. |
|
Don’t blow in anything. It’s as permanent and messy as it sounds.
Rockwool is more expensive but quite frankly you can install it with a butterknife and patience. |
Rockwool. They also have a great technical support line. You could vent it — Home Depot sells different baffle vents. There are some new hemp based products but not yet tested enough. There is some, not a lot, good building science out there (mostly ignored): https://www.energy.gov/eere/buildings/building-america-webinar-stump-building-science-chump-joe-lstiburek-text-version https://buildingscience.com/documents/building-science-insights-newsletters/bsi-095-how-buildings-age |