Anonymous wrote:
The real benefit when turning the heat down is how long it's at equilibrium at the lower temp before it changes back - that's where the savings are. The cost to heat back up was your savings from letting it cool down - those are about a wash.
Anonymous wrote:Anonymous wrote:Anonymous wrote:This site:
https://ashp.neep.org/#!/product/34047/7/25000///0
Has detailed performance specs for that unit.
There are two questions: first is whether the unit has sufficient heating capacity, and the second is which is more economical to run, gas or heat pump.
The answer to the first depends upon what the heating load for your house. On that page you can put in your zip code and the heating load for your house (which your contractor should have calculated) and it will tell you how many hours a year of supplemental heat you'll need and at what temperature you will start needing supplemental heat.
If your contractor didn't calculate a heating load, or it's not available to you, this article tells how to estimate your heating load based on past energy usage and weather:
https://www.greenbuildingadvisor.com/article/replacing-a-furnace-or-boiler
The answer to the second depends upon your local cost of electricity and gas, and the coefficient of performance (COP) of your heat pump. The COP declines as the temperature drops. The page I linked to above shows COP by temperature.
In our climate heating loads are generally higher than cooling loads, if a heat pump was sized for the cooling load it's going to need to be supplemented on the coldest days. The unit you have is rated for 33,800 BTU/hr of cooling at 95F, but only 20,600 BTU/hr of heating at 17F.
Thank you! This is so helpful. Yes our contractor did not want it to be oversized for cooling, this was one of the reasons they recommended dual fuel. I had forgotten about that.
From my eyes as a contractor your contractor had a clue about what they are doing. The bulk would have installed an oversized heat pump. The 25 degree switchover point to gas is a good starting point. You can probably go lower but unless we have an unusually long cold spell or natural gas prices multiply your talking savings measured in the tens of dollars over a winter.
Anonymous wrote:Anonymous wrote:This site:
https://ashp.neep.org/#!/product/34047/7/25000///0
Has detailed performance specs for that unit.
There are two questions: first is whether the unit has sufficient heating capacity, and the second is which is more economical to run, gas or heat pump.
The answer to the first depends upon what the heating load for your house. On that page you can put in your zip code and the heating load for your house (which your contractor should have calculated) and it will tell you how many hours a year of supplemental heat you'll need and at what temperature you will start needing supplemental heat.
If your contractor didn't calculate a heating load, or it's not available to you, this article tells how to estimate your heating load based on past energy usage and weather:
https://www.greenbuildingadvisor.com/article/replacing-a-furnace-or-boiler
The answer to the second depends upon your local cost of electricity and gas, and the coefficient of performance (COP) of your heat pump. The COP declines as the temperature drops. The page I linked to above shows COP by temperature.
In our climate heating loads are generally higher than cooling loads, if a heat pump was sized for the cooling load it's going to need to be supplemented on the coldest days. The unit you have is rated for 33,800 BTU/hr of cooling at 95F, but only 20,600 BTU/hr of heating at 17F.
Thank you! This is so helpful. Yes our contractor did not want it to be oversized for cooling, this was one of the reasons they recommended dual fuel. I had forgotten about that.
Anonymous wrote:This site:
https://ashp.neep.org/#!/product/34047/7/25000///0
Has detailed performance specs for that unit.
There are two questions: first is whether the unit has sufficient heating capacity, and the second is which is more economical to run, gas or heat pump.
The answer to the first depends upon what the heating load for your house. On that page you can put in your zip code and the heating load for your house (which your contractor should have calculated) and it will tell you how many hours a year of supplemental heat you'll need and at what temperature you will start needing supplemental heat.
If your contractor didn't calculate a heating load, or it's not available to you, this article tells how to estimate your heating load based on past energy usage and weather:
https://www.greenbuildingadvisor.com/article/replacing-a-furnace-or-boiler
The answer to the second depends upon your local cost of electricity and gas, and the coefficient of performance (COP) of your heat pump. The COP declines as the temperature drops. The page I linked to above shows COP by temperature.
In our climate heating loads are generally higher than cooling loads, if a heat pump was sized for the cooling load it's going to need to be supplemented on the coldest days. The unit you have is rated for 33,800 BTU/hr of cooling at 95F, but only 20,600 BTU/hr of heating at 17F.
Anonymous wrote:We got a heat pump (a Lennox XP20) with an auxiliary gas furnace this year and I'm a little unclear on the following:
1. In the winter, should we keep the temperature exactly the same throughout the day and night? Or can we lower it a couple degrees overnight/during the workday?
2. The default settings are for the furnace to start "helping" the heat pump when the temp drops below 50 degrees and for the furnace to work on its own below 25 degrees. Do people just use trial and error to figure out the best settings?
3. In the summer, if a heat pump is in cooling mode can we use it like a regular AC (e.g. turn it off or turn up the thermostat when we are not home)?